Harmonic Distortion Problems in Current Distribution Systems
1APIC Power & Energy Innovation Forum
ATCO experiences by Case Muskens
Epcor experiences by Isabella Ciocoiu
FortisAlberta experiences by Gordon McKinlay
Telus experiences by Dwayne Schultz
U of A research findings by Wilsun Xu
APIC 2011 Power & Energy Innovation Forum
APIC 2011
Harmonic Load Growth in ATCO Electric POD Substations
by Case Muskens
APIC 2011
Overview:
PurposeMeasurement IEEE 1459Result SummariesConclusions
APIC 2011
Purpose:
Establish trending of harmonic load growth in the AE system
Evaluate different measurement methods discussed in IEEE 1459
Future implications
APIC 2011
Project Description:
6 substations monitored in 2004 Repeat measurements in 2011 at same substations Review changes
APIC 2011
Measurement Methodology
The ION meter captures hourly RMS values of load, %THDV, %THDI at the main substation transformer
One second waveform snapshots were recorded during the measurement time and processed per IEEE 1459 power definitions
APIC 2011
IEEE Std 1459 2000 : IEEE Standard Definitions for the Measurement of Electric Power Quantities Under Sinusoidal, Non Sinusoidal, Balanced or Unbalanced Conditions
A brief overview of this standard is now provided
APIC 2011
VIS =
vip =
+
=kT
pdtkT
P
1
Power Definitions Single Phase IEEE 1459
Apparent Power
Instantaneous Power
Active Power
Power FactorS
PPF =
APIC 2011
21
22 VVVH =
21
22 IIIH =
1V
VTHD HV =
Harmonic Voltage
Harmonic Current
THDV
THDI1I
ITHD HI =
APIC 2011
The apparent power :
Fundamental effective power:
Non fundamental effective power:
eee IVS = 3
111 3 eee IVS =21
22eeeN SSS =
18
)(3 222222 cabcabcbae
VVVVVVV
+++++=3
2222ncba
e
IIIII
+++=
where
Power definition for 3 phase systems
APIC 2011
Substations Land Location Load type
Flyingshot 702T Grande Prairie MixedHangingstone 701T Ft. McMurray MixedMichichi 703T Drumheller MixedHigh Level 701T High Level MixedNorcen 701T Red Earth OilfieldBrintnell 901T Wabasca Oilfield
Mixed refers to residential + commercial with some light industrial
APIC 2011
High Level Brintnell Flyingshot 2004 2011 2004 2011 2004 2011
THDi% 7.136 5.462 2.56 4.446 5.43 4.856 THDei% 11.96 9.24 2.76 5.04 8.58 8.32 SeN KVA 466 411 590 679 1484 2004 SeN/Se1 % 11.96 9.7 3.05 5.317 8.67 8.4 THDv% 1.61 0.896 1.226 1.703 1.4 1.4 THDev% 0.88 1.698 1.18
APIC 2011
Norcen Hangingstone Michichi 2004 2011 2004 2011 2004 2011
THDi% 2.3 1.37 4.73 6.31 3.32 3.758 THDei% 2.38 1.92 8.32 10.95 4.59 5.174 SeN KVA 267 185 1046 1796 711 1113 SeN/Se1 % 2.91 2.136 9 11 4.65 5.5 THDv% 1.673 0.945 3.436 1.763 0.81 1.911 THDev% 0.95 1.38 1.877
APIC 2011
0 2 4 6 8 10 120
2
4
6
8
10
12Substation Distortion Summary: THDI vs. Harmonic Pollution Ratio
THDI%
SeN
/Se1
%
20042011
Norcen
Brintnell
Michichi
Flyingshot
Hangingstone
Highlevel
APIC 2011
0 2 4 6 8 10 120
2
4
6
8
10
12Substation Distortion Level: Measured vs. IEEE 1459 Effective Value
THDI%
TH
DIe
%
2004
2011
Norcen
Brintnell
Michichi
FlyingshotHangingstone
Highlevel
APIC 2011
1 2 3 4 5 6 7 80
500
1000
1500
2000
2500Substation Distortion Summary: THDI vs. Pod Nonlinear load
THDI%
SeN
KV
A
2004
2011
Norcen
Brintnell
Highlevel
HangingstoneMichichi
Flyingshot
APIC 2011
Hangingstone has had a 5 Mvar 5th harmonic filter added after 2004 which reduced VTHD but with increased ITHD due to harmonic in feed from 144 kV system.
High Level has had an SVC installed on the 144 kV bus along with an extra line to Sulphur Point substation after 2004, SCR has improved.
Brintnell had a pseudo 12 pulse cancellation scheme (mixed Dy and Yy transformers) with the original pad site loads, but the 5th harmonic has been increasing suggesting reduced effectiveness with new loads
APIC 2011
0 0.5 1 1.5 2 2.5 3 3.5 4 4.5 50
1
2
3
4
5
6
7
8
9
10High Level Substation 701T History Start date Sept 8, 2004/2011 4:00 PM
days
%TH
D o
r M
VA
%THDI phs 2 2004
%THDV phs 2 2004
MVA Loading 2004%THDI phs 2 2011
%THDV phs 2 2011MVA Loading 2011
APIC 2011
0 1 2 3 4 5 6 7 8 9 10 110
5
10
15
20
25Hangingstone Substation 701T History Start date Sept 1, 2004/2011 6:00 PM
days
%T
HD
or M
VA
%THDI phs 2 2004%THDV phs 2 2004
MVA Loading 2004
%THDI phs 2 2011
%THDV phs 2 2011MVA Loading 2011
APIC 2011
0 0.5 1 1.5 2 2.5 3 3.5 40
5
10
15
20
25
30
Brintnell Substation 901T(2004) and 902T(2011)History Start date Sept 10, 2004/2011 6:00 AM
days
%T
HD
or
MV
A
%THDI phs 2 2004
%THDV phs 2 2004
MVA Loading 2004%THDI phs 2 2011
%THDV phs 2 2011
MVA Loading 2011
APIC 2011
Conclusions: Despite a load increase at Flyingshot, the harmonic
pollution ratio (%SeN/Se1) has remained nearly constant Hangingstone, Brintnell, and Michichi have seen
increases in the harmonic pollution ratio High Level and Norcen have seen reductions in the
harmonic pollution ratio Harmonic pollution ratio is nearly equivalent to THDIe% The THDIe% is a better indicator than THDI% of actual
harmonic load penetration
Telephone Interference Epcors cases
by Isabella Ciocoiu
Contributing Factors:
9th (main contributor) and 15th harmonics produced by small, single phase, electronic, residential loads;
Position of the telephone cable to the power lines (they run in parallel);
Length of the parallel path (3 or more miles);
Strength of the magnetic field.
2005-2006Telephone Interference on
Ellerslie Road
12EEast Industrial
17 St34 St
50 St66 St101 St
23 E25P
Ellerslie Road
17 St34 St
Telus telephone line
-2005 April: I*T=5300-2005 November: I*T=3000-2006 March: I*T=2600-2006 April: I*T=1800-2006 December: I*T=1000
Noise complaints
Telus cabinet
75 St
91 St
53003000
What Epcor did on its circuits:
1. Balanced loads on 3 phase circuits. 2. Fixed several broken neutral connections. 3. Installed more grounds. 4. Conducted a trial at the substation
transformers, adjusting the taps to increase the bus voltage (25kV to 25.8 kV): eliminated the suspicion that saturated transformers are the cause of harmonic currents.
5. Reduced the load on 23E by transferring about half of the load to another circuit.
2006-2010Telephone Interference on
41Ave
12E (20MVA)East Industrial
17 St34 St
50 St66 St101 St
23 E (17.5 MVA)25P
Ellerslie Road
Telus telephone line
-2006 Dec: I*T=1000-2007 March: I*T=1800-2009 Sept: I*T=2300-2010 July: VAC=105V
Noise complaints
Telus cabinet
75 St
91 St
Dec 2006 -7 Sept 2010
Measured induced voltage
41 AveI*T levels
12E (1.1 MVA)
East Industrial
Summerside
103 GI
17 St34 St101 St
91 St 66 St 50 St
21SU (3.46 MVA)
11SU (11.67 MVA)
12SU (2.16 MVA)
7 September 2010 - 5 November 2010
104 GI
23E (2.4 MVA)
Telus telephone line
Telus cabinet
Noise complaints
75 St
Ellerslie Road
41 Avenue
-2010 Sept 17: I*T=3600
I*T levels
12E
East Industrial
Summerside 103 GI
17 St34 St101 St
91 St 66 St 50 St
21SU
11SU
12SU
5 November 2010 - 24 November 2010
104 GI
23E
Telus telephone line
Telus cabinet
Noise complaints
75 St
Ellerslie Road
41 Avenue
4546S
-2010 Nov 19: I*T=3500
I*T levels
12E
East Industrial
Summerside
17 St34 St101 St
91 St 66 St 50 St
21SU
11SU
12SU
After 24 November 2010
104 GI
23E
Telus telephone line
Telus cabinet
Noise complaints
75 St
Ellerslie Road
41 Avenue
4546S
-2010 Nov 29: I*T=5000
93 GII*T levels
What Epcor did: Approached APIC for technical support in
investigating the telephone interference problem;
Provided distribution system models and facilitated field measurements.
Harmonic Issues in FortisAlberta Service Area
by Gordon McKinlay
1. Trends in Harmonic Distortion in FortisAlb